Quote Originally Posted by CaptCrash View Post
Value 1 20 deg ADC 1 677
Value 2 30 deg ADC 2 304
OK, these ADC values are correct, the calibration has been recovered now

maybe you did not confirm with "yes" at the end of the calibration, this may explain why the values had not been restored immediately. This works usually without any probblem.

The ProfiLuxControl is showing somethingabout 38°C, and I guess ProfiLux is showing ***, which means that the probe is not present or defective. (ProfiLuxControl is not able to recognize that the probe is defective, that is the reason why it shows a wrong value instead of ***).

-> conclusion: if probe is plugged in the correct port then the plug of the probe may be damaged (please check the pins of the PS/2 plug). If you are able to open the plug and check if the wires are OK then do so (this would save us all money and time), if not then the probe must be replaced. I am sorry I can't tell you something else.