Based on your screenshots and where you have the dosing pumps assigned on the sockets, it is not setup correctly.
In your screenshot, you have port S5-8 enabled. This setup would work if you were to move your dosing pump channels to socket 25. You need to uncheck the S5-8 box and check the S1-4 box to activate this port. Once you do that, the dosing pumps should respond to your set schedule. You can test this by using the MANUAL OVERRIDE feature.
If that does not work, go through steps 1-8 and make sure S1-4 is selected and your dosing pump number begins at 5.
TIP: The TIMER functions you are using now do not offer the same level of flexibility of the DOSING PUMP channels. If you move your dosing schedules over to the DOSING PUMP channels, you will be able to monitor your container fluid levels, calibrate the motors, and more.