I have successfully installed the Analog 4 Channel outlet to my system. I have the 4 channel outlet plugged into S1-S4 socket on the P3 and I am using Sockets 1-4 for the analog device. In addition I have the 6 channel Digital (non PAB) bar along with a 4 channel slave dosing pump.
Here is where I need help. I want to add a 6 channel digital PAB powerbar to the system. Can I configure it as follows?
S1-S4 4 Outlet Analog Bar
S25-S30 6 Outlet Digital Bar (Non-PAB)
S31-S36 6 Outlet Digital Bar PAB
S37-S40 4 Pump Slave Doser
How would I set this up such that all devices work in harmony? If it makes a difference I have two other PAB devices (Vortech Controller and the Profilux Touch) in the system.
If there is a better way to configure this please advise.
Thank you in advance for your reply.
Instead of the above configuration I set things up as follows:
S1-S4 OPEN/NOTHING (Can't have an analog device setup on or plugged into a digital channel)
S5-S8 4 Outlet Analog Powerbar (Plugged into S5-S8 port on P3, defaults to S5, S6, S7 and S8)
S9-S14 6 Outlet Digital Powerbar (Non-PAB)
S15-S18 4 Pump Slave Doser*
S19-S24 6 Outlet Digital PAB Power Bar
Everything is working as expected and I reached my goal of adding a second 6 outlet digital powerbar to the system. Thanks to Reefbytes.com for insisting on the PAB vs. the standard digital powerbar. It would have been much more difficult to program a power bar into the system given the 24 channel limitations when using analog and digital (non-PAB) devices together.
*I was originally attempting to program my doser to S21-S24 but the system would not allow me to do so. Why is that?
Last edited by Rotknee; 30.12.2012 at 01:29.
Reason: solved problem after many hours of reading...lol