    Increase the voltage set in the 1-10V interface.

    If no go set the off point to 10%, there is little viewable dimming curve below 15% generally


    GHL ProfiLux Canada/USA Distribution and support

  2. #12

    Default

    Quote Originally Posted by aqua_digital View Post
    Increase the voltage set in the 1-10V interface.

    If no go set the off point to 10%, there is little viewable dimming curve below 15% generally
    they are flickering after they pass 15%. What do you mean by increasing the voltage?
    Right now I have it set at 1 min and 10 max? How do i set the off point at 10%?
    Also I am using version 4.05 does this matter should I update?
    Thank you, jimmy

  3. #13
    Join Date
    18.02.2009
    Location
    Kaiserslautern
    Posts
    7,710

    Default

    increase the min voltage, e.g. 3V

  4. #14
    Join Date
    12.09.2009
    Posts
    6

    Default weird problem

    Hi, i have a little problem with the electronic ballast, my fixture have 2 electronics ballast, only on one, when they start, from 1% to 9% they work well, when they past then 10% the light shut off, and stay off, until a unplug the ballast, if i start the ballast a 20% and higher it work well.

    the other one with exact the same setting and voltage, same tube, work well at all %

    what ?????

    i install your relay to shut off ballast.

    Denis

    ps, i try to exchange the tube from one ballast to the other and the probleme say to the same ballast.

  5. #15
    Join Date
    18.02.2009
    Location
    Kaiserslautern
    Posts
    7,710

    Default

    exact ballast type?