    Default Propellor Breeze with two nominal values.

    Hi

    I'm running a propellor breeze over my sump and it normally keeps the temp constant to the temperature set on the profilux.

    Because of the high temperatures we've been experiencing recently I would like to install to install another propellor breeze that would come on should the temperature exceed the set a set limit.

    For example, the nominal value for temp 1 is 27 degrees. If for any reason the temperature climbed to 28 degrees then the second propeller breeze would come on.

    Thanks

    Rob

  2. #2
    Join Date
    06.02.2012
    Posts
    2,020

    Default

    Create a virtual sensor (setup has to be done in PL device menue, not possible via PLC) and use different settings for the second propeller breeze.