Propellor Breeze with two nominal values.
Hi
I'm running a propellor breeze over my sump and it normally keeps the temp constant to the temperature set on the profilux.
Because of the high temperatures we've been experiencing recently I would like to install to install another propellor breeze that would come on should the temperature exceed the set a set limit.
For example, the nominal value for temp 1 is 27 degrees. If for any reason the temperature climbed to 28 degrees then the second propeller breeze would come on.
Thanks
Rob
-
Create a virtual sensor (setup has to be done in PL device menue, not possible via PLC) and use different settings for the second propeller breeze.