    Default Connecting the Dosing pump after the powerbar

    Ok i programmed my powerbar first, using s1-s4 digital , the sockets 1 to 6 for the power bar. Now this month i'll start dosing; so i unpluged the powerbar OFF the s1-s4 digital and conected the dosing pump and programed it socket 7 to 10 for the 4 dosing pump. When i replug the bar on the s1-s4 and the dosing pump s5-s8 , the only pump starting are 1 and 2, pump 3 and 4 are inactive. What am i doing wrong..? thanks , the rest works great.

  2. #2
    Join Date
    20.02.2009
    Location
    Almacelles
    Posts
    150

    Default

    Quote Originally Posted by Basile View Post
    Ok i programmed my powerbar first, using s1-s4 digital , the sockets 1 to 6 for the power bar. Now this month i'll start dosing; so i unpluged the powerbar OFF the s1-s4 digital and conected the dosing pump and programed it socket 7 to 10 for the 4 dosing pump. When i replug the bar on the s1-s4 and the dosing pump s5-s8 , the only pump starting are 1 and 2, pump 3 and 4 are inactive. What am i doing wrong..? thanks , the rest works great.
    You can't use the Dosing Unit on S5-S8 in this configuration. You have to do this:
    1. Go to Menu and say Yes to Use Digital Powerbar
    2. Then connect the Digital Powerbar to main, and connect the control cable from S1S4 to the Digital Powerbar
    3. Set numbering starting at 1 (sockets from 1 to 6)
    4. Plug off digital powerbar, and connect the control cable from S1S4 to the Dosing Unit, plug the dosing unit to main
    5. Set numbering to dosing unit, starting at 7 (pumps from 7 to 10)
    6. Plug again digital Powerbar to main, and use another control cable to connect the Dosing Unit with the Digital Powerbar
    7. Now you will be able to use the sockets form 1 to 10. Nothing connected to S5S8

    If you want to use S5-S8 with the dosing unit, you will have to program the Digital Powerbar using Set Numbering but starting at 9. The you would have sockets from 5 to 14

    That's all
    GHL Iberia

  3. #3
    Join Date
    10.08.2009
    Posts
    8

    Default

    Quote Originally Posted by Coralleida View Post
    You can't use the Dosing Unit on S5-S8 in this configuration. You have to do this:
    1. Go to Menu and say Yes to Use Digital Powerbar
    2. Then connect the Digital Powerbar to main, and connect the control cable from S1S4 to the Digital Powerbar
    3. Set numbering starting at 1 (sockets from 1 to 6)
    4. Plug off digital powerbar, and connect the control cable from S1S4 to the Dosing Unit, plug the dosing unit to main
    5. Set numbering to dosing unit, starting at 7 (pumps from 7 to 10)
    6. Plug again digital Powerbar to main, and use another control cable to connect the Dosing Unit with the Digital Powerbar
    7. Now you will be able to use the sockets form 1 to 10. Nothing connected to S5S8

    If you want to use S5-S8 with the dosing unit, you will have to program the Digital Powerbar using Set Numbering but starting at 9. The you would have sockets from 5 to 14

    That's all
    Ok thanks, Just did that, the pump seems to be on, but not moving, i've set my dosing at 5ml - 1ml/min 1/day but when does it dose, do i have to set a time or something. I'm asking because before the pump was running non stop , now it just on but no running, am i making any sense, the power is on and its says " com " with the powerbar, but the dosing machanism is not activating.

  4. #4
    Join Date
    18.02.2009
    Location
    Kaiserslautern
    Posts
    7,710

    Default

    before continuing you should do a simple test:
    can you activate the pump manually with ProfiLuxControl (under "socket functions" activate "manual override" then click on the dot left to the socket number)

    now you should know to which socket number your pumps are assigned to