    Default New to this, could use some help!

    Hi everyone,

    I just took receipt of a new 3.1N and hooked it up with my wife on Friday evening. Figured out the illumination and basic functions very quickly - and am very impressed. Then I ran into a roadblock:

    Here's my issue - I have my Return Pumps 1 & 2 connected to PAB Socket 1 (tank is an RSM 250)
    Heater is connected to PAB Socket 2
    Skimmer is connected to PAB Socket 3
    Spectrapure ATO system connected to PAB Socket 4.
    Socket 5&6 are currently blank.

    I've gone into maintenance 1 and named that as my Water Change and it turns off Socket 1, 3, and 4. Perfect.

    I'd like to delay the start of Socket 3 for 3 minutes after water change (so my skimmer doesn't go crazy) and Socket 4 for 5 minutes after water change (gives time for all the water levels to settle). Essentially, I want to delay the start of pumps AFTER Maintenance 1 has ended. I've tried about 40 different configurations and never get the delayed start - please help me correct what I'm doing wrong.

    If anyone could walk me through this logic that would be great. Screenshots are an added bonus! Thanks in advance for your help - and please keep in mind I'm a programming idiot so please feel free to talk down to the most basic level.

  2. #2
    Join Date
    25.12.2011
    Posts
    30

    Default

    Will the blockout delay solve the problem ?

  3. #3
    Join Date
    21.06.2011
    Location
    South Florida
    Posts
    827

    Default

    I think the blackout delay only works if power goes off.



    Doggydoc

  4. #4
    Join Date
    14.02.2013
    Posts
    6

    Default

    Yep, I tried the blackout delay and that didn't work. In my reading, it appears that blackout delay is indeed only for full power outages. If only the programmable logic was, well, logical - or the manual took some time to explain it. I've even looked at the Prog-Logic guide and it did little to help. I'd really, REALLY, like to have this solved soon. Any help would be greatly appreciated.

    Gary

  5. #5
    Join Date
    25.12.2011
    Posts
    30

    Default

    Levelsensor? Water to high skimmer doesnt work the same for the pumps. Progamming with PL.

  6. #6
    Join Date
    14.02.2013
    Posts
    6

    Default

    Not sure I understand the last comment? I'm specifically looking for help with the programming logic. This really can't be that hard for someone that understands the unit really well (unlike me).

  7. #7
    Join Date
    20.02.2009
    Location
    Christchurch
    Posts
    410

    Default

    Quote Originally Posted by TheGolfBallKid View Post
    Not sure I understand the last comment? I'm specifically looking for help with the programming logic. This really can't be that hard for someone that understands the unit really well (unlike me).
    Hi have a look at this post. (just did a search for start delay) Start Delay.
    If you can't get it from this, just ask about which part you don't understand and I should be able to help.
    Call me Paul !
    Note: I am not GHL staff!

  8. #8
    Join Date
    14.02.2013
    Posts
    6

    Default

    That makes sense for Feed Pause ( and I believe there is only 1 FP program available). Can this be done with the Maintenace modes ( of which there are 4)? It seems that this type of programming can't be done to Maintenance - which really wouldn't make sense. If that's the case, the I'll have to use FP for maintenance and vice versa.....

  9. #9
    Join Date
    20.02.2009
    Location
    Christchurch
    Posts
    410

    Default

    If you go to programmable logic, you will see that you can select the pump you want (Skimmer), then you select the type of action(Delay) this can then be set in seconds.
    The description in the other post is just that, a description for that user on why he has it configured, in fact the delay will happen regardless of how the unit is turned (either feed pause or maintenance).
    And there are also 4 feed pauses available.

    Not sure if you have read the manual, but have a look here. Specifically the programming guide and the programmable logic.
    Call me Paul !
    Note: I am not GHL staff!

  10. #10
    Join Date
    14.02.2013
    Posts
    6

    Default

    So here's what I tried after re-reading the manual as well as the above posts:

    Programmable logic 1: input - Filter 2 (skimmer)
    Delayed on
    20 seconds (to test)

    Socket 3: Assigned to PL 1

    Turned on Maintenance mode, and all pumps turned off. Then shut down the maintenance program and ALL pumps - including the skimmer, turned on immediately. Followed the directions to a "T". - what have i missed?