    Default Too many expansion cards!

    Hello,

    I bought a PLM-ADIN extension card, a PLM-Humidity-Temp and a PLM-Oxygen.
    I have a ProfiLux 3 eX with firmware is 5.11 and a Expansion Box

    In the ProfiLux 3 eX there is space for 2 extension cards so one has to go to the Expansion box.
    The problem is that when I switch on the ProfiLux 3 eX no extension card is recognized (PLM-ADIN or PLM-Humidity-Temp or PLM-Oxygen makes no difference).

    What can be?

    Tank you very much in advance!

  2. #2
    Join Date
    06.02.2012
    Posts
    2,020

    Default

    Try another slot. As I know one of the slots does not work with intelligent cards.

  3. #3
    Join Date
    08.01.2013
    Posts
    11

    Default

    Already tried but doesn't work...

  4. #4
    Join Date
    08.01.2013
    Posts
    11

    Default

    now it seems to work, with the Oxygen card in "Modul 4".
    But why wasn't working for Oxygen or ADIN or T&Humidity in "Modul 0, 1, 2, 3"?

  5. #5
    Join Date
    19.02.2009
    Posts
    2,976

    Default

    The PLM-Oxygen generally works in module slot 0 to 4
    The PLM-ADIN/PLM-Humidity-Temp would only work in slot 0 to 3

    It is important to follow these steps, if you add a new card in the ExpansionBox:
    - remove the power supply to the ExpansionBox and open the case
    - put in the module card(s) - be sure the module card is inserted properly (all pins of the module card are in the slot)
    - close the case and reconnect the power supply
    - reassign the ExpansionBox (via PAB menu) to your ProfiLux - only in this case the changes (new cards, removed/moved cards) are detected by the ProfiLux
    - As a result of the changes, the sensors in the ProfiLux change too and must adjusted in the ProfiLux again
    Last edited by GHL Support; 31.01.2013 at 07:51.

  6. #6
    Join Date
    08.01.2013
    Posts
    11

    Default

    Thank you for the reply. Anyway I really tried the three different PLM from the slot 0 to 3 also reassigning the Expansion Box but it hasn't work.
    Then at the end I tried the PLM-Oxygen with the slot 4 and after reassigning the Expansion Box a couple of time, the Profilux found it.

    Anyway now it works and it is already in the pilot plant. Since I have no intention (for now) to use new Expansion Card, it is ok like this!