    Ausrufezeichen Problem with setting Skimmer off with level sensor 1

    Hi everybody,

    I have a problem with setting protection for skimmer.

    I would like to take off skimmer with level senor 1. When water in sump is too high the skimmer should be off.

    I've set:
    Level control as "return pump" with reset errors automatically and Sensor 1
    Socket function for S5 - Fill Water 1 with inverse and blackout delay 0

    When the water is too high, system change socket 5 to off but after several seconds socket is turn on again :-(
    Alarm status is still on.

    Second question.
    How to set in Maintenanse mode to ignore alarms from level sensors?

  2. #2
    Join Date
    20.02.2009
    Location
    Christchurch
    Posts
    410

    Default

    From What I can see, it all seems OK.
    Maybe you have a max on time set, which would then be reverse for you?
    Set max on time to 0 and maybe that will help?

    As for the second question! That has been requested a few times and I was expecting it in the 5.15 release. Though this has not been done.
    So currently there is no way to switch off alarms for level etc when carrying out maintenance.
    (Which seems pretty basic really)
    Call me Paul !
    Note: I am not GHL staff!

  3. #3
    Join Date
    02.01.2012
    Location
    Warsaw
    Posts
    123

    Default

    I set max on time on 8h. Now is better ,skimmer is off but there is no alarm status. :-( maybe in future mathias resolve this problem :-)


    Sent from my iPhone 5 using Tapatalk

  4. #4
    Join Date
    21.06.2011
    Location
    South Florida
    Posts
    827

    Default

    Waiting on that also

  5. #5
    Join Date
    18.02.2009
    Location
    Kaiserslautern
    Posts
    7,710

    Default

    I don't think that we are talking a problem or missing software features, these are just wrong settings

    return pump is the wrong mode for this purpose, that's why you used it in inversed mode

    use ATO (socket not inversed!) and set the max. on-time to a time which is long enough to fill up to the full level in any case

    if you want an alarm permanently then switch off "auto reset alarm"


    second question: maintenance and level alarm

    level alarms are already deactivated during maintenance!
    No support or warranty issues over PM! Please send PMs to the moderators only if you have general problems with using the forum! Thanks for helping us to keep the support efficient.
    Kein Support oder Reklamationsabwicklung über PM! Bitte senden Sie an die Moderatoren nur PMs bei allgemeinen Problemen mit der Verwendung des Forums! Danke dass Sie uns dabei helfen, den Support effektiv zu gestalten.

  6. #6
    Join Date
    02.01.2012
    Location
    Warsaw
    Posts
    123

    Default

    Thanks mathias :-)

    For me it's not a problem with set invert mode - I understand why is that :-)

    Problem was with on time parametr. I've set 'on time' 2seconds. So, When water level in sump was to high the level sensor 1 switched off skimmer without alarm . After 2 sec of working system turn skimmer on and alarm on too.

    I understand why you do that - for protection - in situation when failed level sensor can disable socket for long time.




    Sent from my iPhone 5 using Tapatalk

  7. #7
    Join Date
    20.02.2009
    Location
    Christchurch
    Posts
    410

    Default

    Quote Originally Posted by Matthias View Post
    level alarms are already deactivated during maintenance!
    Ah OK. I read through the documentation and there was no change for this!

    So the alarms are all deactivated, i.e. if I do maintenance on tank 1 which has level 1 & 2, it will shut down alarms for all tanks with level control??
    Call me Paul !
    Note: I am not GHL staff!

  8. #8
    Join Date
    18.02.2009
    Location
    Kaiserslautern
    Posts
    7,710

    Default

    yes, any maintenance deativates all level alarms
    No support or warranty issues over PM! Please send PMs to the moderators only if you have general problems with using the forum! Thanks for helping us to keep the support efficient.
    Kein Support oder Reklamationsabwicklung über PM! Bitte senden Sie an die Moderatoren nur PMs bei allgemeinen Problemen mit der Verwendung des Forums! Danke dass Sie uns dabei helfen, den Support effektiv zu gestalten.

  9. #9
    Join Date
    10.10.2013
    Posts
    994

    Default

    Quote Originally Posted by Matthias View Post
    yes, any maintenance deativates all level alarms
    Except flow sensor alarm :-(

    Could you correct that in next release please?

    Thank

  10. #10
    Join Date
    19.02.2009
    Posts
    2,976

    Default

    Please post this in our customer's wishlist section - thanks.
    No support or warranty issues over PM! Please send PMs to the moderators only if you have general problems with using the forum! Thanks for helping us to keep the support efficient.
    Kein Support oder Reklamationsabwicklung über PM! Bitte senden Sie an die Moderatoren nur PMs bei allgemeinen Problemen mit der Verwendung des Forums! Danke dass Sie uns dabei helfen, den Support effektiv zu gestalten.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •