Let us start at the beginning and forget the previous posts - too confusing in my opinion
in general: ATO and AWC works for all sensors in the system, incl. Expansion Box
the setup depends on the used firmware, as I can see in these screenshots you are using 5.14, right?
The Expansion Box must be assigned correctly. If a firmware update either of the Expansion Box or the ProfiLux has been made in the past it is possible that the assignment isn't correct anymore.
I recommend this:
- save settings and sensor data first
- bring ProfiLux and Expansion Box to the newest firmware version and update ProfiLuxControl if not already happened
- reset PAB
- assign PAB devices
- load settings back
thelevel sensors are numbered as follows:
- ProfiLux onboard level sensors (e.g. 1 + 2)
- sensors of the first EXB (e.g. 3 + 4)
- and so on
please check the newest programmers guide 5.14
next step: check the sensor assignments of the level control you want to use
do the ATO or AWC settings now - let us go from here