    Default Socket setup for NR

    Hi all
    I want to run a Dosing pump as the feeder of water from sump into a nitrate reactor and have a probe measure the redox in the NR. Then what I would like to do is switch pump on when the redox is at level A let's say -150mV and when it gets to -100mV switch the pump off and let the NR work and once the reading is -150 switch dozing pump on again.... Thus keeping the NR happy and working at optimum levels.

    Is -150 ~-100 the best range and any tips on how to program this on the p3 with a stand alone Rosing pump being switched via a pab 6 power bar?

    Help needed on how to program this function in the P3????

  2. #2
    Join Date
    20.02.2009
    Location
    Almacelles
    Posts
    150

    Default

    Why don't you use the easiest function:
    Redox Nominal Value: -150
    Redox Hysteresis: 80 (or 100)
    Socket function: Redox1 -> Increase value
    GHL Iberia

  3. #3
    Join Date
    06.09.2011
    Posts
    33

    Default

    Thank you, have just installed the pump and done the programming will monitor for the next few hours.