    Default Turning socket on with delay after feed-pause or maintenance

    Dears,

    How can help me to implement the following?
    I would like to stop my skimmer during feed-pause and maintenances and restart it after several minutes.
    My socket is assigned to Filter and react well to feed-pause.
    The socket is also switched to off during maintenance 1 and maintenance 2.

    Now i would like to restart the skimmer after 60 minutes after the feed-pause and after 5 minutes for maintenance 1 and maintenance 2.

    I was able to delay it after a feed-pause but not with both.

    Thank u in advance

  2. #2
    Join Date
    18.02.2009
    Location
    Kaiserslautern
    Posts
    7,713

    Default

    then you need 2 gates of the prog. logic

    1: maintenenace inverse AND filter
    2: prog logic 1 delayed on

    use prog logic 2 for the socket in question
    No support or warranty issues over PM! Please send PMs to the moderators only if you have general problems with using the forum! Thanks for helping us to keep the support efficient.
    Kein Support oder Reklamationsabwicklung über PM! Bitte senden Sie an die Moderatoren nur PMs bei allgemeinen Problemen mit der Verwendung des Forums! Danke dass Sie uns dabei helfen, den Support effektiv zu gestalten.

  3. #3
    Join Date
    02.02.2011
    Posts
    39

    Default

    Hi Matthias,
    Thank u but the goal is to have a delay on different for the feed-pause and for the maintenance.
    I just want to wait few minutes after a maintenance (wait the return pump job) and delay for 1 hour after feeding.
    best regards
    - Geoffroy



    100X60X50 (cm) - 300 l. total net volume
    Profilux 3 + Dosing Pump - PH & Temp Probe - Level - 2 Powerbar 6D
    ATI Powercone 200 - Vertex UF-15 biopellet loaded
    Giesemann Matrix 8 X 39w



  4. #4
    Join Date
    09.07.2010
    Location
    Aschaffenburg
    Posts
    987

    Default

    In that case you need tree gates of the prog. logic:

    1. Maintenenace [inverse] delayed on for a few minutes
    2. filter delayed on for a hour
    3. prog logic 1 AND prog logic 2


    Use prog logic 3 for the socket in question

  5. #5
    Join Date
    02.02.2011
    Posts
    39

    Default

    Thank u, i will test it and let you know.
    - Geoffroy



    100X60X50 (cm) - 300 l. total net volume
    Profilux 3 + Dosing Pump - PH & Temp Probe - Level - 2 Powerbar 6D
    ATI Powercone 200 - Vertex UF-15 biopellet loaded
    Giesemann Matrix 8 X 39w



  6. #6
    Join Date
    07.06.2009
    Posts
    738

    Default

    shouldn't that be an OR ?

  7. #7
    Join Date
    09.07.2010
    Location
    Aschaffenburg
    Posts
    987

    Default

    shouldn't that be an OR ?
    No. If you use OR, filter will stop never due it´s negative logic.

    If you start feed pause filter will go off and also the socket with delay of one hour
    If you start maintenance, maintenance will go off [have in mind: it´s inverse] and also the socket with delay of a few minutes
    Only if filter AND maintenance[inverse] are active, filter will run. If you would use OR, one input is enought to start filter

  8. #8
    Join Date
    02.02.2011
    Posts
    39

    Default

    if i use the AND then the socket goes off immediately (without invoking maintenance or feed pause).
    If i use OR, then the socket goes off when i invoke maintenance but it doesn't go off when i invoke feed pause.
    ;-(
    - Geoffroy



    100X60X50 (cm) - 300 l. total net volume
    Profilux 3 + Dosing Pump - PH & Temp Probe - Level - 2 Powerbar 6D
    ATI Powercone 200 - Vertex UF-15 biopellet loaded
    Giesemann Matrix 8 X 39w



  9. #9
    Join Date
    09.07.2010
    Location
    Aschaffenburg
    Posts
    987

    Default

    if i use the AND then the socket goes off immediately (without invoking maintenance or feed pause).
    If you aktivate feed pause, socket will go off immediately. If feed pause is over, it will stay of for one hour
    If you aktivate maintenance, socket will also go off immediately. If maintenance is over, it will stay of for a few minutes
    It will stay off until the longest delay time is over

    That´s what I understand you want to have ..... if you want to have something different, please explain.
    I´ve checked function, it should work in that way. If it does not what it should, check programming

  10. #10
    Join Date
    02.02.2011
    Posts
    39

    Default

    Perfect!
    Your solution works well, but i was obliged to assign "always on" to the socket , save, then assign again "Prog logic 3" and save again.
    I think that because the socket was already assigned to Prog Logic 3 before i perform the change of the logic itself, the system might kept the old configuration.

    Now, if i want to assign a delay to a new maintenance , i will have to do the following :
    1.Maintenenace 1 [inverse] delayed on for a few minutes
    2.Maintenenace 2 [inverse] delayed on for a few minutes
    3. filter delayed on for a hour
    4. prog logic 1 AND prog logic 2
    5. prog logic 3 AND prog logic 4

    Thank u again
    - Geoffroy



    100X60X50 (cm) - 300 l. total net volume
    Profilux 3 + Dosing Pump - PH & Temp Probe - Level - 2 Powerbar 6D
    ATI Powercone 200 - Vertex UF-15 biopellet loaded
    Giesemann Matrix 8 X 39w



Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •