    Default how to , deactivate socket on PH alarm

    Hi,

    last year September i had a major fail in my aquarium

    due to a over active level control and a limewater ( calcium water ) filling.
    half my tank died due a PH value of 12.

    last months i still worked without any control on the PH.. and did worked.
    My tank looks better then ever.. but now i want to go the safe way

    at this moment my Level control is running on a timer so only filled at night when under level.

    Now i want to add a PH alarm to it.. so it stops filling limewater when the PH rises to a sertain value.

    How do i set this up.. ik have the PH on a alarm.. but how to set the socket to turn off on the level control
    Profilux 3 Ex

    ProfiLuxControl, Version 5.0.6.0
    Firmware ProfiLux 3, Version 5.06 (GER+ENG)

  2. #2
    Join Date
    09.07.2010
    Location
    Aschaffenburg
    Posts
    987

    Default

    • set ph activity to 'enabled' (you´ve already done that)
    • set up the ph value control values and the hysteresis you want
    • enable and set up the ph alarm as you want
    • set up the socket function of the desired port to 'ph value 1' and 'increase'
    • save it & that´s it.


    If you don´t want to regulate but to switch of at alarm, it´s also possible to set the socket to 'ph value 1', 'Alarm' and 'Switching behavior:invert'

  3. #3
    Join Date
    11.05.2009
    Posts
    77

    Default

    Quote Originally Posted by Wirus View Post
    • set ph activity to 'enabled' (you´ve already done that)
    • set up the ph value control values and the hysteresis you want
    • enable and set up the ph alarm as you want
    • set up the socket function of the desired port to 'ph value 1' and 'increase'
    • save it & that´s it.


    If you don´t want to regulate but to switch of at alarm, it´s also possible to set the socket to 'ph value 1', 'Alarm' and 'Switching behavior:invert'

    This only switch the socket to Ph value
    The socket need to switch on Level indication , which is linked to a timer by it self

    but turned off on a PH alarm
    Profilux 3 Ex

    ProfiLuxControl, Version 5.0.6.0
    Firmware ProfiLux 3, Version 5.06 (GER+ENG)

  4. #4
    Join Date
    07.06.2009
    Posts
    738

    Default

    with the use of logic you can AND together all the input you have
    the ph increase
    the timer
    the level switch


    AND between all of them ( in 2 logic steps => since you can only add 2 entries in a logic step )
    but you can use logic 1 as input of a 2nd one.

    as said before in logic you have increase , decrease or alarm on the probes so you can add the PH alarm in the logic to have 100 % certainty

  5. #5
    Join Date
    11.05.2009
    Posts
    77

    Default

    only one Logical is needed then ( i think )

    Level and PH.
    because the timer is already assigned in Level ATO

    For now i created these settings, which i am going to test on a free socket


    logic.jpgPH.jpgTIMERATO.jpg
    Profilux 3 Ex

    ProfiLuxControl, Version 5.0.6.0
    Firmware ProfiLux 3, Version 5.06 (GER+ENG)

  6. #6
    Join Date
    07.06.2009
    Posts
    738

    Default

    The timer you indicate is the max on time ( if the level hasn't toggled it will give an alarm , it has nothing to do with a timeframe when it can run)

    since he wants to run it @ night he needs a timer to run it then

  7. #7
    Join Date
    11.05.2009
    Posts
    77

    Default

    The timer i indicate is programmed to turn on ( or not if level is oke ) every hour for 10 minuntes after 22:00

    Yes the max ontime is also programmed there ,( but not just that )
    Profilux 3 Ex

    ProfiLuxControl, Version 5.0.6.0
    Firmware ProfiLux 3, Version 5.06 (GER+ENG)

  8. #8
    Join Date
    11.05.2009
    Posts
    77

    Default

    Yeah i got it working!

    its like i thought..

    Level contol as it was ( on the timer )
    and PH on a alarm 8 PH with 0,5 as Alarm

    A programmable Logic Water 1 AND PH value 1 ( inverted in my case )

    on the socked where the level pomp is connected this programmable Logic ..

    just tested this.. works like a charm!
    Profilux 3 Ex

    ProfiLuxControl, Version 5.0.6.0
    Firmware ProfiLux 3, Version 5.06 (GER+ENG)