    The manual for the LED-1 states that to get the unit to respond on the secondary port (L2,4,6) you need to move the jumper inside the box.
    However, there are two jumpers inside. Which one should be moved?

  2. #2
    Join Date
    19.02.2009
    Posts
    2,976

    Default

    Hi

    please have a look at the excerpt of the user manual LED-Control:
    "You can set by jumpers on the circuit board in the inside of the electronics if it shall react on L1 (resp. L3, L5, L7) – therefore put jumper on 1 and 2 – or on L2 (resp. L4, L6, L8) – set jumper on pin 2 and 3. According to the factory settings, both jumpers are put on pin 1 and 2."
    -> so you have to put both jumpers onto pin 2 and 3 insteat of 1 and 2.

  3. #3
    Join Date
    12.08.2009
    Posts
    27

    Default

    Thank you Carolin. That is what I have done but it was not clear from the documentation. The documentation does not mention either two jumpers, or the fact that both should be setup the same way.