    Default Temp1 probe 30F off

    Hello,

    I recently installed a Profilux III unit and the water temperature probe (temp1) is reading 30F higher than actual water temperature. I understand that this probe is factory callibrated and shouldn't need field adjustment. Can anyone tell me if adjustment is possible, however, or is this probe simply malfunctioning?

    Thank you,
    Chad Peeling

  2. #2
    Join Date
    20.02.2009
    Location
    Ottawa, Canada
    Posts
    127

    Default

    I had the same problem one time check to see if the probe is calibrated for pond or aquarium. (Not in Profilux Control but in the menus of the controller)

  3. #3
    Join Date
    18.02.2009
    Location
    Kaiserslautern
    Posts
    7,710

    Default

    as Xiaan mentioned it is possible that you accidentally used the wrong measurement range "Pond" - then set it back to "Aquarium"

    or you changed manually the offset (with adjust offset in ProfiLuxControl)

    next option: probe is plugged into level port

    last idea: probe defective, not very likely