Thread: Activating digital connecting

  1. #1
    Join Date
    07.03.2010
    Location
    Nederland
    Posts
    62

    Default Activating digital connecting

    Hello Profilux-users,

    I have a question about using the digital connection for the dosingunit.

    On S1-S4 I have connected a standard STDL-4 powerbar. On S5-S8 a 4 unit dosingunit. I want to use the digital connection for the dosingunit.

    When I want to activate digital control on S5-S8 via PLC 5.0.1.1 I get a warning: if an STDL-4 is connected on S1-S4 (like I have) it will be damaged.
    (Can someone please explain why it will be damaged? I really want to understand it.)

    So I thought: connect the dosingunit on S1-S4 and the standard powerbar on S5-S8. This results in the same warning: if a standard powerbar is connected on S1-S4 it will be damaged.

    I suppose this implicates that this combination can work but is this true?
    So what is the correct way to connect the dosingunit digitally and the STDL-4 non digital?

    The latest programming guide (FW 5.00) only describes a digital connection on S1-S4. So I think it's not up to date. Or have I overlooked something?

  2. #2
    Join Date
    07.03.2010
    Location
    Nederland
    Posts
    62

    Default

    Isn't there anyone who knows the answer to this question..?

  3. #3
    Join Date
    30.05.2009
    Location
    Langen (Hessen)
    Posts
    34

    Default

    Hello,

    you have to connect the digital dosing unit on S1-S4 and the standard powerbar on S5-S8. Only S1-S4 can be activated and used for digital outlets.

    Kai

  4. #4
    Join Date
    07.03.2010
    Location
    Nederland
    Posts
    62

    Default

    Hello kugelfisch,

    Thanks for your reply.

    You said only S1-S4 can be configured for digital connections but in PLC 5.0.1.1 S5-S8 can be configured the same way.

    So I want to be really sure how to connect both units and keep them both healthy and working properly in this changed/updated (FW en PLC) environment. The warnings prevent me from changing these settings.
    As I wrote earlier, unfortunately the latest manual doesn't give the answer.

  5. #5
    Join Date
    30.05.2009
    Location
    Langen (Hessen)
    Posts
    34

    Default

    Hallo Martin,

    you are right. In PLC 5.0.1.1 you can activate S1-S4 and/or S5-S8 for digital communication. You can damage a non-digital-powerbar, if you activate the digital connection for this. The German information in the message box -concerning this matter- is clear.

    I think you don't read the message correctly:

    If you activate S1-S4 to digital communication, the message box warns, that a non-digital-powerbar on S1-S4 can be damaged.

    If you activate S5-S8 to digital communication, the message box warns, that a non-digital-powerbar on S5-S8 can be damaged.

  6. #6
    Join Date
    07.03.2010
    Location
    Nederland
    Posts
    62

    Default

    Hi kugelfisch. Thanks for your reply.

    Underneath the English message that appears when S5-S8 is selected for digital connection.



    I've tried to change the language setting of PLC to German, but despite saving this setting and restarting PLC, it's keeps talking in English...

    But do I understand it right that the same warningbox in German speaks twice about S5-S8 in this matter?

  7. #7
    Join Date
    18.02.2009
    Location
    Kaiserslautern
    Posts
    7,710

    Default

    thanks for the hint - this typo error will be fixed in a new PLC version

  8. #8
    Join Date
    07.03.2010
    Location
    Nederland
    Posts
    62

    Default

    Matthias,

    Thanks for the confirmation. The dosingunit is now digitally connected.