    Frage Bottom heater

    Can someone clarify how the GHL operates with a bottom heater?

    According to the manual the bottom heater takes precedence over the heater. The heater is switched on only when the bottom heating alone is inadequate.

    This feature is potentially useful to me, as I have a heatpump that is the prefered heating method, with titanium heating elements as a backup. So I could set the heatpump as the "bottom heater" and the titanium heaters as the "heater".

    But I am unclear exactly when/how the GHL determines the bottom heater can't cope and kicks in the main heater. Is there a built in time lag? Or does it wait for the temperature to drop even further? What is the logic process the GHL follows before turning on the main heater?

    Thanks,

    Keith

  2. #2
    Join Date
    18.02.2009
    Location
    Kaiserslautern
    Posts
    7,710

    Default

    there are 2 temperature levels: one activates the heater, if the temp. falls below the second level the bottom heater will be switched on. Both have a overlapping hysteresis.

  3. #3
    Join Date
    10.04.2009
    Posts
    4

    Default

    Quote Originally Posted by Matthias View Post
    there are 2 temperature levels: one activates the heater, if the temp. falls below the second level the bottom heater will be switched on. Both have a overlapping hysteresis.
    Thanks Matthias, could you confirm my understanding using the following example?

    My "nominal value" is 26C, with a hysteresis of 0.4C. So if the bottom heater would turn on at 25.8C at what temperature would the heater activate - 25.6C ?

    Regards,

    Keith

  4. #4
    Join Date
    19.02.2009
    Posts
    2,976

    Default

    With a hysteresis of 0.4 C, the heater would be activated at temp<25.8 C (botton heater then already switched on). At temp>26.2 C, the botton heater will be switched off (heater then already switched off).

  5. #5
    Join Date
    10.04.2009
    Posts
    4

    Default

    Quote Originally Posted by Carolin View Post
    With a hysteresis of 0.4 C, the heater would be activated at temp<25.8 C (botton heater then already switched on). At temp>26.2 C, the botton heater will be switched off (heater then already switched off).
    Sorry, please bear with me, I just want to make sure I am getting this right.

    So as temperatures fall the bottom heater is activated at 26C, the heater at 25.8C? And as temperatures start to increase the heater will go off at 26C and at 26.2C the bottom heater will also go off? Correct?

    Keith

  6. #6
    Join Date
    19.02.2009
    Posts
    2,976

    Default

    Yes, correct.

  7. #7
    Join Date
    10.04.2009
    Posts
    4

    Default

    Quote Originally Posted by Carolin View Post
    Yes, correct.
    Thank you for your patience!

    Regards,

    Keith

  8. #8
    Join Date
    29.06.2009
    Location
    Longmont, CO
    Posts
    76

    Default What if you've only got One Heater?

    I've only got one heater in my tank...

    Should I have the Profilux use that as "bottom heater" so that it comes on soonest and begins heating, or should I have it as just the "normal heater"

    Thanks

  9. #9
    Join Date
    20.02.2009
    Location
    Almacelles
    Posts
    150

    Default

    Normal heater. Bottom heater function is designed for bottom heaters