    Ausrufezeichen Important - updates over USB

    Important - updates over USB

    If you are trying to do firmware updates over USB please remove the data lead from S1S4 and PAB prior to doing the update, this also applies to S5S8

    After doing this please continue with the update over USB to USB.

    Some users reported drop outs when attempting to do firmware updates over USB, the reason for this has been found that certain devises spike when switching off creating a USB signal drop out, by unplugging the cable no spike can occur.

    The next firmware version will have an auto shut off built in prior to the upload starting.


    GHL ProfiLux Canada/USA Distribution and support

  2. #2
    Join Date
    10.03.2009
    Posts
    478

    Default

    S5-S8 should also be removed

  3. #3
    Join Date
    05.05.2009
    Posts
    57

    Default

    I removed all leads prior to upgrading from 5.00K to 5.01B and tried upgrading it on USB but it still crashed so i went the flasher using RS232, this still seems to be the best way at the moment.