    Default Issue connecting Doser 2.2 EXT

    I have an existing Profilux 4 with two Doser 2 EXT units on the PAB as 1-4 and 5-8. I have added a new doser and it’s a 2.2 EXT model and while it is showing in the PAB configure screen the settings cog doesn’t appear next to it like it does for the other dozers, so I can’t set it to 9-12. It’s responding on 1-4 just fine and running identically to the existing Doser 2 already configured on those channels. My Profilux is latest firmware 7.25 and I’ve tried many power on/off cycles on the doser and the Profilux. The 2.2 EXT is running firmware 1.46. How can I change the start channel number for it?
    Last edited by SusanParrot; 29.07.2023 at 08:20. Reason: Correct post Title for 2.2 instead of 2

  2. #2
    Join Date
    10.10.2013
    Posts
    1,003

    Default

    Hello Susan,

    The problem is that the firmware on your ProfiLux is too old.

    The latest is 7.36, available with the latest GHL Control Center here: https://www.aquariumcomputer.com/dow...enter-1-1-4-7/

    Update procedure: https://www.aquariumcomputer.com/kno...ux-4-firmware/

    If you have any problems, please open a support ticket at https://www.aquariumcomputer.com/sup...ets-enquiries/ (Guest login).

    Gaël
    Last edited by Gael; 29.07.2023 at 09:08.
    No support or warranty issues over PM!
    Please send PMs to the moderators only if you have general problems with using the forum! Thanks for helping us to keep the support efficient.

    Creating a support ticket
    For support or warranty issues, create a support ticket by clicking here.

  3. #3
    Join Date
    29.07.2023
    Posts
    3

    Default

    Thanks Gael,
    I did exactly that before posting, and 7.25 is the (latest) firmware version it offered me. How can I update to a newer version (7.36) when the GHL Control Centre says I'm already running the latest firmware?
    [Edit] I might try upgrading GHL Control Centre to see if it gives me a newer firmware option for my Profilux.
    Thanks.
    Last edited by Gael; 29.07.2023 at 09:08.

  4. #4
    Join Date
    10.10.2013
    Posts
    1,003

    Default

    Yes, as I told you, you need to update GCC first.

    Gaël
    No support or warranty issues over PM!
    Please send PMs to the moderators only if you have general problems with using the forum! Thanks for helping us to keep the support efficient.

    Creating a support ticket
    For support or warranty issues, create a support ticket by clicking here.

  5. #5
    Join Date
    29.07.2023
    Posts
    3

    Default

    After upgrading GHL Control Center to the latest version I was able to upgrade the Profilux to 7.36 (current version).
    Then I restored the settings from file backup.
    The system is back running normally, but the PAB assign page is now blank - no PAB devices showing at all (although they are working correctly).
    I tried a power cycle of the Profilux, didn't change.
    I updated my iPhone app to the latest version and reconnected, same - no PAB devices showing at all now.
    What is the next step?
    Thanks

  6. #6
    Join Date
    10.10.2013
    Posts
    1,003

    Default

    Once you're on the page of currently assigned devices, when you click on the assign button, the window that opens where you can check off the devices to be assigned is empty?
    If so, please open a support ticket at https://www.aquariumcomputer.com/sup...ets-enquiries/ (Guest login).

    Gaël
    No support or warranty issues over PM!
    Please send PMs to the moderators only if you have general problems with using the forum! Thanks for helping us to keep the support efficient.

    Creating a support ticket
    For support or warranty issues, create a support ticket by clicking here.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •