Originally Posted by
Vinny
Hi,
The ATO function already has a built-in fail safe called Max on-time.
If your reservoir were to run dry, the ATO pump would only run based on a max allowed time. Once this limit expires, you will get an alarm notification via the flashing red light, email, and/or text.
If you'd like you can leave the sensor in the reservoir assigned to the Leak detection function. Just don't forget to enable "inverted" on that sensor.
Once the water level reaches that sensor, it will trigger the alarm.
All of the above does not require you to use any PL functions.
If you still choose to run it the way you have it now, that PL setup will work as long as the leakage sensor in the reservoir is set to inverted.