Thread: Tunze Streams not controlled by Profilux 4

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Join Date
    27.04.2017
    Location
    Nyon, Switzerland
    Posts
    75

    Default Tunze Streams not controlled by Profilux 4

    I have recently purchased the Profilux 4 (Ultimate) and am very happy with the functionality that I have been able to use so far (the Touch screen can do with a major upgrade: the resolution of that screen is very 1990s :-)).

    I am however having a problem getting the Profilux to control my two Tunze Stream 6055s in my 250 liter reef tank. I have connected the Tunze 1 and Tune 2 cables to them and these cables are in turn connected to the Y splitter which is then connected to the L1/L2 port on the Profilux. One of the Tunze streams is a more recent one and has the Turbelle controller to which I attached the Tunze 1 cable at the top and set the controller to "outside control". The second stream is an older model without the controller and I just connected the Tunze cable directly to the little breakout box.

    I have assigned the 1-10v ports 1 & 2 to be Stream Pump 1 and Stream Pump 2. I also changed the voltage (after seeing other posts about this) to min 3v max 8v.

    I then assigned Pump 1 and Pump 2 to Stream Group 1 with a minimum of 40% and maximum of 80% for each pump.

    Here is the problem: the pumps seems to be constantly at the same speed all of the time, no matter which mode I choose. Even choosing "No current" (which I assume to mean that they should be off) doesn't change anything. When I unplug the Tunze cable 1 and Tunze cable 2 from the Y splitter, the pumps keep working at the same speed.

    I tried to move the Y splitter to the L3/L4 connection on the Profilux. Then both Stream pumps stopped working!

    What have I missed?

    Any help would be appreciated!

    Thanks!

    Laith

  2. #2
    Join Date
    27.05.2015
    Posts
    2,488

    Default

    Hello Laith,

    Have you tried swapping the T1 and T2 cables?

    Please post screenshots of the 1-10V interface page and stream group 1 page.

  3. #3
    Join Date
    27.04.2017
    Location
    Nyon, Switzerland
    Posts
    75

    Default

    Hello Vinny,

    Yes I did try swapping the T1 and T2 cables and there was no difference.

    By the way, when I moved the splitter cable from the L1/L2 port to the L3/L4 port and both pumps stopped working I had not programmed or assigned those ports at all. So something is happening with the L1/L2 port, it must be communicating something?

    Here are the screenshots. The screenshot of the Stream Group settings is in two parts, top and bottom.

    1-10v screenshot.jpg
    Stream Group top.jpg
    Stream Group bottom.jpg

    Thanks!

    Laith

  4. #4
    Join Date
    27.05.2015
    Posts
    2,488

    Default

    Connect them back to the L1/L2 and select a wave mode.
    I see you don't have anything selected; choose either Right-angled or Sinus wave.

  5. #5
    Join Date
    27.04.2017
    Location
    Nyon, Switzerland
    Posts
    75

    Default

    Ok, I'll try that when I'm back at home next to the tank.

    So if I understand you correctly, in order to use one of the modes (permanent, permanent opposite, sequence 1 etc) you have to select a wave mode?

  6. #6
    Join Date
    27.05.2015
    Posts
    2,488

    Default

    Yes. Otherwise, the pumps won't alternate between the min/max settings.