Thread: Flow sensor not acknowledged

  1. #1
    Join Date
    03.02.2018
    Posts
    10

    Default Flow sensor not acknowledged

    I plug the sensor in to the green socket. Assigned flow sensor 1 to connection 1. Calibrated it to 12.4 for my 9000 l/m unit and no flow indicated.

    Can anyone tell me what I’m doing wrong


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    27.05.2015
    Posts
    2,488

    Default

    From our P4 Programming manual

    7 Flow
    ProfiLux 4 allows you to connect Flow sensors to our controller. These can be connected to the permanently installed level inputs 1 or 2 and to ProfiLux Expansion cards with level inputs.



    By having the flow sensor connected to the green port, you have it connected to LEVEL 3/4 which is incorrectly connected.
    Connect your flow sensor to the purple port, LEVEL 1/2.

  3. #3
    Join Date
    03.02.2018
    Posts
    10

    Default

    Quote Originally Posted by Vinny View Post
    From our P4 Programming manual

    7 Flow
    ProfiLux 4 allows you to connect Flow sensors to our controller. These can be connected to the permanently installed level inputs 1 or 2 and to ProfiLux Expansion cards with level inputs.



    By having the flow sensor connected to the green port, you have it connected to LEVEL 3/4 which is incorrectly connected.
    Connect your flow sensor to the purple port, LEVEL 1/2.
    Man thanks Vinny I'm such an idiot....All is working fine. Thanks for a quick response

  4. #4
    Join Date
    19.01.2015
    Location
    Barcelona, Spain, Spain
    Posts
    21

    Default

    Hi!!
    To take advantage of the thread ... would it work with the Splitter Cable for Level Sensors (PL-LY)?
    Thanks

  5. #5
    Join Date
    27.05.2015
    Posts
    2,488

    Default

    PL-LY splitter cables can be connected to any LEVEL port.

    2 flow sensors can be connected to level 1/2 and to a 4Level expansion card.

  6. #6
    Join Date
    19.01.2015
    Location
    Barcelona, Spain, Spain
    Posts
    21

    Default

    Ah! Ok, but, last question, Can I use the splitter, connecting the Flow Sensor and a Level Sensor?
    Or in other words, can I connect two different sensors (flow and level) to each end of the splitter?
    Thank you very much

  7. #7
    Join Date
    13.08.2010
    Posts
    4,150

    Default

    Yes, all you have to do is assign them to the correct port

    regards Pit

  8. #8
    Join Date
    20.05.2017
    Posts
    63

    Default

    Hi
    Will the flow sensor work on Expansion Box which is connected to a P3 ex? My other level ports are occupied

  9. #9
    Join Date
    27.05.2015
    Posts
    2,488

    Default

    If the expansion box has the PLM-4Level expansion card installed, yes.

  10. #10
    Join Date
    18.01.2019
    Posts
    29

    Default

    I conneced the flow sensor to splitter cable at the purple port and to the purple side , at the green port the level aensor is conn , its not working