Thread: ProfiLux 3: What to do in the case a firmware update failed

  1. #31
    Join Date
    18.02.2009
    Location
    Kaiserslautern
    Posts
    7,710

    Default

    thanks for sharing your experience!
    We know that some USB-RS232-converters are just not working with every hardware, that makes it sometimes not easy for us to give support when connection problems occur.

    yes, ProfiLux must reboot (power off/on) after updating the firmware with the recovery tool

  2. #32
    Join Date
    07.06.2009
    Posts
    738

    Default

    Just to let you know it worked for me via the Serial , usb was not possible.

    All hail to serial !!!!

  3. #33
    Join Date
    19.01.2010
    Posts
    44

    Default No Power

    Failed in firmware upgrade. Proceeded as instructed but when resetting P3 failed to power up. Plugged and unplugged many times. No power.

  4. #34
    Join Date
    18.02.2009
    Location
    Kaiserslautern
    Posts
    7,710

    Default

    Proceeded as instructed but when resetting P3 failed to power up
    what do you mean? After resetting the P3 in download mode all lights are off. This is normal.

  5. #35
    Join Date
    19.02.2009
    Posts
    39

    Default

    I tried using the flash and it asks to specifythe hex file???

  6. #36
    Join Date
    19.02.2009
    Location
    MANOTICK
    Posts
    866

    Default

    The HEX file is the file you wish to upload, the new firmware file

    1. download http://www.aquariumcomputer.com/Download/Flash-FR.zip
    2. save it somewhere you will find it, no installation required
    3. start "flash.exe"
    4. select "MB91F467D" as controller, 4MHz, navigate to the firmware file (click "open")
    5. check the interface (under "set environment")
    6. disconnect ProfiLux 3 from power (it is not necessary to open the enclosure and to set a jumper like it was ProfiLux II!)
    7. now click "full operation" - ProfiLux still has no power!
    8. plug in the DC-connector - ProfiLux has now power again and the download should start

    Hint: If the update with ProfiLuxControl failed then there is maybe something wrong with your connection from PC to ProfiLux 3. Please ensure that your connection is stable and reliable before attempting to update with ProfiLuxControl or this tool, e.g. check the USB driver and update it if possible.


    GHL ProfiLux Canada/USA Distribution and support

  7. #37
    Join Date
    19.02.2009
    Posts
    39

    Default

    i realize that but when I run the FLASH software the line that says HEX file is blank!

  8. #38
    Join Date
    19.02.2009
    Location
    MANOTICK
    Posts
    866

    Default

    install fware to desktop then press open on the hex file and select the fware you have just dowloaded to your desk top


    GHL ProfiLux Canada/USA Distribution and support

  9. #39
    Join Date
    28.03.2010
    Posts
    11

    Default

    I had to bring my profilux to work to get access to a serial port after updating over usb failed. Appears to be working now, although I don't know how I'm going to update it again in the future

  10. #40
    Join Date
    19.02.2009
    Location
    MANOTICK
    Posts
    866

    Default



    GHL ProfiLux Canada/USA Distribution and support