    Default How to connect 3th flow sensor to Profilux 3.1T ex

    I have two PL-LY splitter.
    The first splitter I connected to "Level 1&2" socket. And connect two flow sensor there. It works OK.
    The second splitter I connected to "Level 3&4" socket. And connect level sensor ( it works OK ) and trying connect 3th flow sensor.

    The GCC does not see 3th flow sensor. It can only 1 and 2 choose at the page 'Profilux - Flow-sensor'.
    There are only 1 or 2 to choice on the 'connected at level sensor' column

    How to connect 3th flow sensor to Profilux 3.1T ex?

  2. #2
    Join Date
    06.02.2012
    Posts
    2,020

    Default

    Unfortunately the 3th level input can´t be used for a flow sensor, you need a level expanison card for that. From the manual of the PL:

    4 Flow
    You can connect flow sensors to the ProfiLux. They can be connected to the built-in level-inputs 1 or 2 and to
    expansion cards with level-inputs.
    Up to 4 flow-sensors can be connected to the ProfiLux 3-models.
    As you can see, level input #3 isn´t named.