Originally Posted by
CaptCrash
My configuration is setup to deliver the following:
Water top up will only occur if the Filter 1 setting is active. This means that during a maintenance and a feed pause the top up process is suspended.
Top up will only occur if the level sensor is in the sump is low and will last for a maximum of 60 seconds.
Water must be low for 2 seconds before a top up will be initiated.
If the in sump level sensor is low and the conductivity needs to be increased (salinity of the water is below the target less the hysteresis value) and there is water above the level of the sensor in the salt water top up container, then the salt water top up pump will be turned on. The turn on time is limited to 1 minute and will stop 2 seconds after the in sump level sensor reaches the desired level or if the salt water top up container water level is lower than the sensor.
Alternately if the in sump level sensor is low and the conductivity needs to be decreased (salinity of the water is NOT below the target less the hysteresis value) and there is water above the level of the sensor in the RO water top up container, then the RO water top up pump will be turned on. The turn on time is limited to 1 minute and will stop 2 seconds after the in sump level sensor reaches the desired level or if the RO water top up container water level is lower than the sensor.
In your case, if you don’t have level sensors in the top up containers, don’t use Programmable Logic 14 and Programmable Logic 15 and change the socket configurations as listed below.
If you do have top up sensors and your sensors are configured differently to mine (e.g. not using digital inputs) you may need to invert signals, change the programmable logic as applicable and/or change the activation times etc for your setup.
In my case this is primarily use to deliver salt water back into the system as I remove fish from my grow out system (I breed fish), plus deal with the day to day evaporation/RO top up requirements. I also run this on my breeding setups, but it is rare that they use the salt water top up.
The settings I have are as follows
System Configuration
Profilux 3 Ex
Firmware Version 6.18
Level Sensor for sump water level 1
Socket for RO Top Up S5
Socket for Salt Water Top Up S6
Filter 1 controls return pump
Salt water container water level Digital Input 1
RO Top Up container water level Digital Input 2
Level Sensor Settings
Control Circuit 1
Operational Mode Auto Top Up
Maximum On Time 0:01:00
Reset error Automatically ticked
Auto Top off (ATO) Always active ticked
Used sensors for this control 1
Reaction Time 2 Seconds (set at bottom of the screen)
Programmable Logic 10
Input 1 Fill Water (ATO) 1
Input 2 Conduct.(S) 1 Increase
Invert NOT ticked
Function AND
Description Top Up with Salt Water
Programmable Logic 11
Input 1 Fill Water (ATO) 1
Input 2 Conduct.(S) 1 Increase
Invert ticked
Function AND
Description Top Up with Salt Water
Programmable Logic 12
Input 1 Programmable Logic 10
Input 2 Filter 1
Function AND
Description Only Top Up Salt Water when Filter 1 ON
Programmable Logic 13
Input 1 Programmable Logic 11
Input 2 Filter 1
Function AND
Description Only Top Up RO Water when Filter 1 ON
Programmable Logic 14
Note: Only use if you have level sensor in Top Up container
Input 1 Programmable Logic 12
Input 2 Digital Input 1
Function AND
Description Only Run if Salt Water in container
Programmable Logic 15
Note: Only use if you have level sensor in Top Up container
Input 1 Programmable Logic 13
Input 2 Digital Input 2
Function AND
Description Only Run if RO Water in container
Socket 5
Programmable Logic 15 (or 13 if you do not have level sensor in Top Up container)
Socket 6
Programmable Logic 14 (or 12 if you do not have level sensor in Top Up container)
Hope this helps/gets you there. If you have issues let me know and I may be able to assist.