    it's possible two program logic for one socket ?

    because i want securited water level for my pump and skimmer but i have program logic 4 on this socket so i can't stop socket when level error ?

    thanks

    program logic.jpg
    profilux socket.jpg
    Attached Images Attached Images
    Last edited by mmaxfr; 10.10.2015 at 22:28.

  2. #2
    Join Date
    27.05.2015
    Posts
    2,492

    Default

    You can have two Programmable Logic commands set on one socket by using a new Gate # and assigning Programmable Logic #4 and which other one you want controlled. This new gate would then be assigned to the socket.

  3. #3
    Join Date
    18.02.2009
    Location
    Kaiserslautern
    Posts
    7,710

    Default

    yes, you can cascade logic gates, which means that the output of one gate can also be the input of another one