I have a tunze cable for even and one for odd pumps. both on there own L port.
I can stop the pump , start , feedtime them etc. But for some reason every other % in the display doesn't seem to have any impact on the current in the displaytank. for example when I set it to a rect wave , I can see the % changing every 5 seconds , but I don't seem to have any impact in the aqua. only on/off seems to work.
Since the beginning I also have been confused by the pumps interface. I have 1 pump in group 1 and 1 in group 2 and I still have 4 pump-lines in the lower screen ???
so this means that the tunze connector box (the motor driver) reacts on the ProfiLux output signal - at least it is switched on and off
ProfiLux can't do more than change the output voltage within the given range (here: 3V...8V), the speed of the tunze pump must follow this signal.
Maybe you try this: change the function of the 1-10V-interface to "illumination 1" (the voltage settings should remain), then change the "brightness" with the manual illumination and watch what happens - does the speed vary?
It appears the pump control does work as intented. I just seems to be a matter of finding a right settings , wave pattern.
with the tunze it was either on/off min max , so the pumps followed a certain pattern. Now with all the profilux settings ( max, thunderstorm, random wave reduction ) it's not so easy to see pump changes as what you expect to see.
So it seems it just a matter of perception, settings-tweaking.