Can GHL build a test unit that all can connect to.
This would rule out the Apps
Printable View
Can GHL build a test unit that all can connect to.
This would rule out the Apps
Jasonk , it's a normal when product (app ) has problems of youth. :-)
I'm a electronic, programmer and IT engineer, I have the same problems in my job :-)
I don't know how looks profilux code, but not long time ago, I had the same problems with our project. We've build internet application. Everything was ok when we've tested app. When project was started commercially, we've noticed problems with mass users logon proccess. We had to rebuild xml code for faster communication structure for client and server side :-)
Sent from my iPhone 5 using Tapatalk
Please check description of each light, sensor and switch. It should not contain any special characters like " / }*{*] [ ' ( ) @ etc.
:cool: IT WORKS...
I did review the descriptions and found many incoherent entries (parts of file names, random characters,...)
To make sure all was cleaned-up, I did the cleanup through the configuration files (using the ProfiLuxControl application, menu [File] --> [Transmit all settings from ProfiLux to file], saved the file on the system, edited the file with a text editor, changed all CODE_DESCRIPTIONS_START (parameters number 18000 to 18127) to be an empty string, saved the file under a new name, loaded it back to the ProfiLux using ProfiLuxControl, ignored the 4 errors for parameters 4203, 4219, 4235 and 4251 CODE_DYNAMICNOMINALVALUE1_SENSORINPABGROUP). NB - these 4 errors are a bit of a worry. This is probably an unsupported method and may even completely break the ProfiLux configuration and operation. But for me it worked !!!
Nice application ! Thank you...
Amazing! I had some much crap in Profilux descriptions, with wired characters etc and after I deleted them, hey presto the App works! (Im not even going to going to ask how all those invalid characters even got there to begin with)
Case closed, Thanks!
tools first always workers blame their
:cool:
I cant even find some of those characters on a keyboard so something must have gone screwy before during an update. :) Regardless, glad GHL came up trumps and happy camper now! (Right, onto pushing for wirelss Mitras PAB device now :))
My app is currently working but I have a strange thing going on with my Temp Graph.... When I go into the graph instead of the normal Up & down blue line showing the temp variations the graph is solid blue (like I used a paint roller to fill in) from 0.0C up to around 77.0C (current temp is 76.4F and desired temp is 76.4F).
Also when it's showing the "Actual Temp" under Sensors > Temperature 1 is shows 76.4F#~ (2 strange characters of # ~).
Any suggestions?
Have you checked the Profilux Descriptions in PLC?