05.03.2009, 10:57
… can be realized as follows:

Pump plug can be clamped at
- a control cable with western plug OR
- LBF-AP

--> in any case set the 1-10V-interface at the ProfiLux to 2,5 – 8,5 V

Here the accessory:
http://www.aquariumcomputer.com/System__E_/Products/Illumination_technics/Lamp_accessories/lamp_accessories.html

Coralleida
05.03.2009, 23:37
Fantastic, good job

aqua_digital
06.03.2009, 04:00
So to clarify this info

The control line of the pump is connected via an LBF-AP box to the ProfiLux 1-10V interface and the 1-10V settings must be set to 2.5v to 8.5v

This gives you full ramp up and ramp down control of the pump :D

Considering the massive array of ProfiLux settings and control for variable pumps this will really interest many users I am sure.

Thanks for sharing the information.