View Full Version : First time setup questions
dwsps180
11.09.2009, 02:32
Hi,
I am trying to setup Profilux Plus II for the first time. I have two questions:
1) Regarding the temp probe. After I connected it, it shows 79.8F however my Ranco shows 78F and my little floating glass therm shows 76F. Does the temp probe needs to be calibrated?
2) Regarding the PH probe. It shows like 5.67 after connected. Does the PH probe also needs to be calibrated for its first use.
Both of the probes are brand new I believe.
Thanks,
GHL Support
11.09.2009, 07:10
1) Regarding the temp probe. After I connected it, it shows 79.8F however my Ranco shows 78F and my little floating glass therm shows 76F. Does the temp probe needs to be calibrated?
No, the temperature sensor usually doesn't need to be calibrated. But if you like to have the sensor show the values of the other thermometers, then you can adjust the sensor to them. Here is how to do this:
http://www.aquariumcomputer.com/Forum/showthread.php?t=357
2) Regarding the PH probe. It shows like 5.67 after connected. Does the PH probe also needs to be calibrated for its first use.
The pH-probe must be calibrated before its first use! Therefore you need two calibration fluids, 4 + 7 for fresh water or 7 + 9 for salt water. In the manual you can read unter pH/Calibration how the calibration works.
dwsps180
14.09.2009, 01:47
Ok, thanks!
Somehow today the temp value is similar to the others so I think it is fine now.
I have the calibrate fluid and will calibrate the PH probe tmrw.
dwsps180
14.09.2009, 02:21
Actually I have some left over Pinpoint PH calibration fluid, can I use those?
GHL Support
14.09.2009, 09:04
Yes, if you have fluids for the two required calibration values, you can use them.
dwsps180
15.09.2009, 15:34
Ok, now that Temp and PH are fine, moving onto software. How do I find out what's the current firmware I have so I can download the correct control software?
Thanks again!
GHL Support
16.09.2009, 07:24
Two possibilities:
1. Disconnect and connect again the power plug of ProfiLux --> the firmware version is displayed
2. Under Extras/Info&Support the version is also displayed
dwsps180
16.09.2009, 13:42
found it, thx!