View Full Version : Water Change settings help firmware 5.15



hemoi
18.12.2012, 08:05
Hi,
I need some help with setting up my water change with the new firmware.

PLC :5.1.5.1
Firmware: 5.15
I have 2 optical sensors. Used for water change and ATO.
Settings as follows:
Sensors:
33413340

Sockets:

3345
The timer trigers AWC no problem and drain process begins. The issue is when the drain operation is complete both sockets 9 and 10 switch on. i.e both fresh water and NSW begin filling.
Is it possible to have it so based on conductivity setting, either fresh water or salt water is activated. This is how i have my prog logic setup.
Or even in the event of a water change just salt water fill is active ?

hemoi
20.12.2012, 04:03
anyone ?

Antipodes
20.12.2012, 07:33
Hi,
Is it possible to have it so based on conductivity setting, either fresh water or salt water is activated. This is how i have my prog logic setup.
Or even in the event of a water change just salt water fill is active ?

I am doing exactly the above and have no problems.
Images below should show how I am achieving it.
3351335233533354

Matthias
20.12.2012, 08:09
these are 2 different ways:

1. use different sockets during refill for ATO and during refill for AWC
I saw you used S9 for "ATO and AWC" and S10 "AWC only"
-> use S9 for ATO only

2. or you use the prog. logic, then you have to combine "ATO and AWC" with "control up" and "control down"

I recommend 1.)

muz_zz
14.01.2013, 10:01
Is it possible to do more than one water change a day with 5.15?
If so could some just explain how it's done
As the only option is to select one timer, is this correct?

Thanks
Maury

Matthias
16.01.2013, 10:21
yes, only one timer can be assigned to the level control (here: AWC)
but this timer can have several times per day to start tis AWC-event

muz_zz
16.01.2013, 10:54
Thank you Matthias
I will setup 2 AWC a day now