Hello,

Can you please tell me if with the ProfiLux 3 with 3 level sensors I can do the ATO and AWC of a freshwater tank and also do the ATO of the RO/DI reservoir?

I'm planning to use 2 level sensors in the sump for ATO (above sensor) and AWC. The third sensor I'll use on the RO/DI reservoir to automatically filling it up using a solenoid valve and an osmosis unit.

Thank you

GHL Support
24.05.2011, 10:15
I'm planning to use 2 level sensors in the sump for ATO (above sensor) and AWC.
Yes, this is possible with two level sensors, using the operation mode "Water change and ATO", you will need two sockets on the powerbar.


The third sensor I'll use on the RO/DI reservoir to automatically filling it up using a solenoid valve and an osmosis unit.
So you just want to fill up water by using one socket at the powerbar? Then you can use the third sensor with mode "ATO".

Please note that you can't connect three level sensors at the ProfiLux 3 (only two possible, with splitter). You would need a ProfiLux 3 ex (you can upgrade with
the extended upgrade) or an Expansion box.

RRodrigues
29.05.2011, 13:48
Thank you Carolin.

richard.mayo
08.06.2011, 04:36
So how does the ATO and AWC work on the Profilux???

RRodrigues
09.06.2011, 09:49
Hello Richard Mayo,

I have being asking this question to help a distant friend seting up is ProfiLux. My friend says that it is working Ok and he is following all the indication that I've obtained from here. Do you have any specific questiong regarding the ATO and AWC?