View Full Version : Water Temp Calibration??



almost
03.06.2010, 18:27
Hi,
I just add to the system :

1. one new expansion box in which I add a temp-hum card with the probe, 1 reedox probe (& calibrate), 1 pH probe(& calibrate), & 1 Conductivity probe (& calibrate)
2. a temp-hum (with the probe) & 2L4S card in the existing (old) expansion box

I also calibrate the probes in the EXIII.

Everything went fine, exept BOTH water temp values. After the modification to the system, both water temps are displaying wrong values.

In main aquarium water temp is 25C, and after the additions it saws 38,9C!!

In support aquarium, water temp is 28,4C and after the additions it saws 38,5C!

I Calibrate both temps with ADC1 value 677 & ADC2 value 319 but it changed to 0, something.

I restart the system twice, wrong water temp in both aquariums..

Need help, want to add 5breeze in support aquarium (just bought with speed control) to cool down the water.




PS: Matthias, I am waiting for the update version in wich I can put a comment beside the probes as I start to forget which one is which. :D Also, in graph display I see pH, in the top, in the middle & to the bottom without even pH1, pH2, pH3. So is very difficult to handlle the system (I want to expand it even more :D ).Here is a print screen:
http://inlinethumb19.webshots.com/46674/2785670460103497988S600x600Q85.jpg (http://pets.webshots.com/photo/2785670460103497988vvCxUI)

chippypah
04.06.2010, 11:46
Did you press save after adding the values ?.
Cheers
Pete

almost
04.06.2010, 12:48
Yes I did, press save & load.


Can't calibrate temp1 through EXIII, when I press calibrate it goes directly to save yes or no.

Also if I change temp value in Temp 1,2 or 3, (pressing the "adjust temp" button) nothing changes.

Try with previous version of PFControll, the same..

Any ideas?

Please?

almost
04.06.2010, 13:18
Maybe I did too much jobs yesterday..:p

Its O.K. now, had put both temp probes to level input.

Lol.


How can I find which L number (L6,L7 etc) is in the expansion box to assign it to temp 2?

Matthias
07.06.2010, 07:38
How can I find which L number (L6,L7 etc) is in the expansion box to assign it to temp 2?

the numbering of all ressources is explained in the Expansion Box manual

http://www.aquariumcomputer.com/System__E_/Download/download.html

almost
08.06.2010, 18:36
O.K.
Get it.

Wish description like page 9 or 11 on manual come out from the profi & not the user.