Hi,
This morning I received an SMS with the following data:
ALARMA!!!!
Temp 1 40.0C *
pH 1 5.95pH
Redx 1 405mV
Co.S 1 1.0049 +
pH 2 8.04pH -
Temp 2 40.0C !
12 4
12 4
12 4
How is it possible?
Thanks
Enviado desde mi Nexus 5 mediante Tapatalk
Hi,
What is the current WiFi module firmware version on your P4?
Have you noticed this happening randomly or during certain times of the day?
Please post a screenshot of this email settings.
Hi Vinny,
I have the 6318 version of the wifi. t
The message has been sent by the sms module.
Today was the first time.
Thanks
Enviado desde mi Nexus 5 mediante Tapatalk
BiTurbo195
20.09.2017, 22:16
Hi,
i have the same Problem once or twice a week.
I thought the Problem was my cabels, i reorganized them but the Problem is still there.
Profilux 4 with WiFI 6407 an Firmware 7.08.
Greets from Germany
Witch components? I used pl3ex with exbox2 temp Sensor digital and have the same problem. U have temp alarm on? If no switch on and show how many times u have alarm with 40°
Gesendet von meinem SM-G955F mit Tapatalk
Matthias
22.09.2017, 07:43
to all:
we had 2 customers recently who had this problem.
It was solved when they moved the temp.-sensor cables away from potential electromagnetic disturbers
(other cables, especially from/to ballasts, pumps, power supplies etc.)
both customers solved that problem with this
-> please avoid interferences for the temp.-sensor (cable), this may interfere with the digital data transmission
-> if this does NOT solve your problem the contact the GHL support directly