    Default Have socket switch of when alarm!

    Hi! I had a faulty tempprobe that showed 0 C and that did that the heater never switched off. I saved the fish becasue the temp reached 34c before I could stop it.

    I would like to program so the heatersocket switches off if the alarm goes off on the tempprobe. I tried with the programable logic but i cant figure it out.

    Help plz

  2. #2
    Join Date
    13.08.2010
    Posts
    4,150

    Default

    you can test it with this config

    logik1.PNG
    logik2.PNG

    regard Pit

  3. #3
    Join Date
    30.03.2011
    Location
    helsingborg
    Posts
    177

    Default

    Thx will try

    Skickat från min G8141 via Tapatalk

  4. #4
    Join Date
    27.05.2015
    Posts
    2,488

    Default

    1. Go to the TEMPERATURE settings page.
    2. In the ALARM section, select ACTIVE to activate the alarm feature for this probe.
    3. Select YES for Deactivate control.
    5. Set the maximum allowed temperature deviation.
    4. Click SAVE CHANGES.

    This will turn off the assigned powerbar outlet in case the temp reading is outside of the allowed deviation.

  5. #5
    Join Date
    30.03.2011
    Location
    helsingborg
    Posts
    177

    Default

    This is what i want. Thank you. Vinny i emaild your support and they didint know this.