Thread: 0-10v return pump controlling problem

  1. #1
    Join Date
    11.12.2016
    Posts
    16

    Default 0-10v return pump controlling problem

    Just got to run the Aquabee DC 5000 with Controller and 0-10v cable, connected to L1/L2 port, following setting post found in forum here, but the pump seems still working with it's own program and not running anything I set in Profilux, should be anything wrong?

    Thank!

  2. #2
    Join Date
    06.02.2012
    Posts
    2,020

    Default

    Not knowing what you have done, the suggestion is that the controller is not set to extern.
    Also maybe the wiring is wrong

  3. #3
    Join Date
    11.12.2016
    Posts
    16

    Default

    Hi,

    The DC pump controller had been connectred to the profilux L1/2, it's set "external" controlled by the aquarium computer(which Profilux 4 is), nothing appeared in the GCC's 0-10v option. I tried plug the 0-10v cable into another yellow L port, (3/4, 5/6) still the same, nothing changed.

    Am I doning anything wrong?

  4. #4
    Join Date
    27.05.2015
    Posts
    2,488

    Default

    The cable that connects directly to the L-port should be one that was designed to use with our ProfiLux controller.

    Any other cable should be first connected to our LBF-AP accessory, then from the LBF-AP to the ProfiLux.

    Since this is connected to the L1/L2 port:
    1. Go to the 1-10V INTERFACE settings page and select L1.
    2. Set the function to STREAM PUMP 1. This will assign the pump as a Stream pump.
    3. Go to an unused STREAM GROUP settings page.
    4. Select PUMP 1 from the RIGHT column and click the LEFT-pointing arrow to assign Stream pump 1 to this Stream group.
    5. Use the Stream group settings page to set the behavioral patterns of your pump.
    6. Save settings.