Thread: Delay after maintenance mode

  1. #1
    Join Date
    07.04.2017
    Posts
    157

    Default Delay after maintenance mode

    I made a simple programming logic always on with delayed power on. Is it possible to make sure this works after disabling / exiting maintenance mode. It then ignores the power delay and turn on the socket right away

  2. #2
    Join Date
    07.04.2017
    Posts
    157

    Default

    Nobody knows if that's an error or intended?

  3. #3
    Join Date
    30.06.2013
    Posts
    111

    Default

    Im in the same boat. Would love to see delay start on my skimmer after i activate maint mode.

  4. #4
    Join Date
    07.04.2017
    Posts
    157

    Default

    Nothing?

  5. #5
    Join Date
    11.06.2017
    Location
    Kaiserslautern
    Posts
    80

    Default

    Could you please upload a screenshot of your setup in maintenance and progr. logic?
    Which socket is assigned with this logic?
    No support or warranty issues over PM! Please send PMs to the moderators only if you have general problems with using the forum! Thanks for helping us to keep the support efficient.
    Kein Support oder Reklamationsabwicklung über PM! Bitte senden Sie an die Moderatoren nur PMs bei allgemeinen Problemen mit der Verwendung des Forums! Danke dass Sie uns dabei helfen, den Support effektiv zu gestalten.

  6. #6
    Join Date
    07.04.2017
    Posts
    157

    Default

    Quote Originally Posted by Marc View Post
    Could you please upload a screenshot of your setup in maintenance and progr. logic?
    Which socket is assigned with this logic?
    Extremely simple setup, Marc. All off during maintenance, and socket function of the skimmer is set to the attached progr. logic.

    Screen Shot 2017-08-02 at 20.43.33.jpg
    Screen Shot 2017-08-02 at 20.41.48.png

  7. #7
    Join Date
    11.06.2017
    Location
    Kaiserslautern
    Posts
    80

    Default

    After exiting the maintenance mode the sockets just get the inputs of the assigned logic. For example, in your case the input is always on, so the socket would be set to on. The function will be ignored.

    Solution:
    Set the input of your logic to maintenance and invert it. Then the socket will be delayed on after maintenance.
    No support or warranty issues over PM! Please send PMs to the moderators only if you have general problems with using the forum! Thanks for helping us to keep the support efficient.
    Kein Support oder Reklamationsabwicklung über PM! Bitte senden Sie an die Moderatoren nur PMs bei allgemeinen Problemen mit der Verwendung des Forums! Danke dass Sie uns dabei helfen, den Support effektiv zu gestalten.

  8. #8
    Join Date
    07.04.2017
    Posts
    157

    Default

    Quote Originally Posted by Marc View Post
    After exiting the maintenance mode the sockets just get the inputs of the assigned logic. For example, in your case the input is always on, so the socket would be set to on. The function will be ignored.

    Solution:
    Set the input of your logic to maintenance and invert it. Then the socket will be delayed on after maintenance.
    But then it wont be delay when cycling the power regularly?

  9. #9
    Join Date
    11.06.2017
    Location
    Kaiserslautern
    Posts
    80

    Default

    When do you want the delay exactly be done? After exiting the maintenance mode and?
    You can interlace more logics to get this solved.
    No support or warranty issues over PM! Please send PMs to the moderators only if you have general problems with using the forum! Thanks for helping us to keep the support efficient.
    Kein Support oder Reklamationsabwicklung über PM! Bitte senden Sie an die Moderatoren nur PMs bei allgemeinen Problemen mit der Verwendung des Forums! Danke dass Sie uns dabei helfen, den Support effektiv zu gestalten.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •