Results 1 to 3 of 3

Thread: Program for ozone generator to turn off if redox is too high

  1. #1
    Join Date
    20.02.2010
    Posts
    18

    Default Program for ozone generator to turn off if redox is too high

    Hi,
    I need help with programming the ozone generator. I want the ozone generator to turn on if redox <375mv and turn off if redox is >400mv. The ORP probe is redox 1 and The ozone generator is plugged in to socket 8 (S8).
    Thanks!

  2. #2
    Join Date
    24.02.2017
    Location
    Freeport
    Posts
    51

    Default

    First you go to sensors, set the control range you would like then save it.Next go to the programming logic select the sensor and falling as the ozone should turn on if the ORP is falling, finally go to your switched outlets, select outlet #8 and set it to programming logic # X , X being the number of which ever logic you set up to control your ORP.

  3. #3
    Join Date
    27.05.2015
    Posts
    2,492

    Default

    1. Go to the Redox settings page and define your desired value and hysteresis. If you want to activate an alarm, do so in the same page and select how much of a swing you will allow before an alarm is triggered.
    2. Go to the Switch channels and outlets page and select the socket where you have the Ozone connected (S8). Set the function to Redox 1 Increase.

    With this setting, your Ozone will react according to the nominal value and hysteresis you set in the Redox settings page.